Hi everyone,

I’ve been comparing multi vs single-zone models, and I might have spotted a problem with the `HB Blend ProgarmTypes` component. I think the averaging method works fine for the design load capacities, but fails at the schedule level, yielding loads that do not respect load conservation.

The component is basically doing:

```python
program = ProgramType.average(name, _programs, _ratios_)

```

[This](https://www.ladybug.tools/honeybee-energy/docs/_modules/honeybee_energy/programtype.html#ProgramType.average) goes through every load and applies the corresponding averaging method. For simplicity, take [how this works for People objects](https://www.ladybug.tools/honeybee-energy/docs/_modules/honeybee_energy/load/people.html#People.average). In short, it calcuates the people density, radiant fraction, latent fraction, occupancy schedule, and activity schedule using the input floor area ratios as weights. In other words, the following weight is applied to both load capacities and schedules:

w\_{zone}=\frac{A\_{zone}}{A\_{total}}

The problem is that averaging the occupancy density and schedule independently does not necessarily conserve the actual number of occupants!!! If we impose an occupancy balance between the original zones and the equivalent single zone, this is actually what we should get:

A\_{\mathrm{eq}}D\_{\mathrm{eq}}S\_{\mathrm{eq}}(t) =\sum\_i A\_iD\_iS\_i(t)

Since the blended design occupancy is already conserved, we obtain:

\boxed{ S\_{\mathrm{eq}}(t)= \sum\_i \underbrace{\frac{A\_iD\_i}{\sum\_j A\_jD\_j}}\_{w\_i}S\_i(t) }

where A\_i is the floor area, D\_i the design occupancy density, and S\_i(t) the occupancy schedule. In the case of People, we can write the schedule weight as:

w\_i=\frac{N\_i}{N\_t}

where N\_i is the amount of people in zone _i_ and N\_t the total amount of people in the building.

In other words, **the occupancy schedules should be weighted by their contribution to the total design occupancy, rather than just the floor-area ratios.**

In my case, the blended single zone model had almst 30% more occupied hours than the original multizone model, despite having exactly the same design occupancy. I imagine the same issue could arise for lighting and equipment when different programs have different power densities and schedules.

Wouldn’t it make sense to use load-weighted schedules in the averaging methods to ensure conservation of the time-dependent loads? Or am I missing something here?