# Looking to create a simple passive test cell with NO Mechanical Ventilation

**URL:** <https://discourse.ladybug.tools/t/looking-to-create-a-simple-passive-test-cell-with-no-mechanical-ventilation/19323>\
**Category:** ladybug-tools\
**Tags:** honeybee, natural-ventilation\
**Created:** [August 22, 2022, 12:56am UTC](https://discourse.ladybug.tools/t/looking-to-create-a-simple-passive-test-cell-with-no-mechanical-ventilation/19323 "2022-08-22T00:56:41Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![MichaelDonn](https://discourse.ladybug.tools/user_avatar/discourse.ladybug.tools/michaeldonn/32/95_2.png) [@MichaelDonn](https://discourse.ladybug.tools/u/MichaelDonn)\
**Post date:** [August 22, 2022, 12:56am UTC](https://discourse.ladybug.tools/t/looking-to-create-a-simple-passive-test-cell-with-no-mechanical-ventilation/19323/1 "2022-08-22T00:56:41Z")

</div>

I have posted on this topic before, but responses there are not helping solve this issue:

> [@Honeybee Energy and Natural Ventilation appearing as a substantial cooling component in the Energy Balance](https://discourse.ladybug.tools/t/honeybee-energy-and-natural-ventilation-appearing-as-a-substantial-cooling-component-in-the-energy-balance/14272):
>
> Hi All I feel again I will be pointed towards a solution that already exists somewhere on this discussion board, but my search cannot find it. I am running a simple energy balance with Ideal Loads on a five zone commercial building floor. I cannot get the openable windows to contribute more than a tiny fraction to the cooling. I have chosen to define ventilation capability in the program (in terms of ACH - setting the other ventilation inputs such as flow per person etc to zero)- and…

I am looking to create a simple model with a large shipping container box (12.2m x 2.4m x 2.6m ) to which students will apply different fenestration treatments and natural ventilation options and construction properties. I am adapting the Sample files for this situation. For example:  
[Test\_annual\_loads\_2.gh](https://discourse.ladybug.tools/uploads/short-url/8tXrZoiO1xISlNPOrD3A5jc6Ra0.gh) (111.2 KB)

 ![image](https://discourse.ladybug.tools/uploads/default/original/3X/3/b/3b401e23424e93c74629db147117901ceb4f1490.png)

(NOTE: the test .gh file has the external shade objects disconnected. The model brep (pink circle) should be linked to a box drawn in Rhino (I use surface extruded) or to the container .3dm file also enclosed.  
[Container\_Large.3dm](https://discourse.ladybug.tools/uploads/short-url/cfj6nBMsGvjvrPh8YAugZEFeNLz.3dm) (159.6 KB)  
 ![image](https://discourse.ladybug.tools/uploads/default/original/3X/3/7/379d1a8174930ce7646ff5de1ffb9f74bc062936.png)

What I am looking for is a way of using the HB Annual Loads component to establish a Passive energy balance, not this, where “mechanical ventilation” is dominant:

 ![image](https://discourse.ladybug.tools/uploads/default/original/3X/b/0/b052289635a30906412ceccbf7d1ff7f9177724a.png)

Ventilation control for the above looks like this:

 ![image](https://discourse.ladybug.tools/uploads/default/original/3X/3/a/3a0e0b3710f8a49ddb0b692b7e03cab8fbc46a86.png)

The following results from making a change to Vent Control settings:

 ![image](https://discourse.ladybug.tools/uploads/default/original/3X/8/8/889cdf416054019e46d26e642d8ca507c09d785b.png)

The settings for this are:

 ![image](https://discourse.ladybug.tools/uploads/default/original/3X/1/9/19f1d46c49a3530224ac054c8703a276dcef3558.png)

Further along the line for these results I have set the following:  
 ![image](https://discourse.ladybug.tools/uploads/default/original/3X/b/e/be92465a32142482df98db92017f3d24a2afecfa.png)

It was my expectation that if I set these ventilation settings to zero, then more use would be made of openable windows. But, no.  
A quick trial of setting JUST the vent\_per\_person value to 10l/s/person and disconnecting the vent\_ACH and the vent\_per\_floor inputs produces the following:

 ![image](https://discourse.ladybug.tools/uploads/default/original/3X/c/8/c87d8e77049e9dcb9c5bc04d12ea4c81e0cecf48.png)

I confess that I am not really understanding how to understand these input parameters to manage and explain my demonstration file.

I can ‘explain’ “Mechanical Ventilation” as merely the need to supply minimum fresh air requirements. But the storage terms indicate an error in my inputs, and I am surprised by how slight the natural ventilation cooling energy is.

Any help you can offer would be gratefully received.

---

<div class="post-metadata">

**Author:** ![charlie.brooker](https://discourse.ladybug.tools/user_avatar/discourse.ladybug.tools/charlie.brooker/32/27164_2.png) [@charlie.brooker](https://discourse.ladybug.tools/u/charlie.brooker)\
**Post date:** [August 22, 2022, 12:15pm UTC](https://discourse.ladybug.tools/t/looking-to-create-a-simple-passive-test-cell-with-no-mechanical-ventilation/19323/2 "2022-08-22T12:15:16Z")

</div>

Hi @MichaelDonn,

I think I’ve seen this at some point on the forum before. The mechanical ventilation component of the Load Balance for a default Ideal Air system (the default system applied) includes an air side economizer (or an approximation of how one would operate) controlled on Dry Bulb temperature.

So even when you set all the input parameters for ventilation to 0, the free cooling aspect of the mechanical ventilation system still exists by default.

If you plug in your room to the Ideal Air System component you can remove this economizer, which removes the mech vent portion from your loads.

 ![image](https://discourse.ladybug.tools/uploads/default/original/3X/7/0/703e8ea99c3471844a88201d536ad3ad30191146.png)

Default Ideal Air System

 ![image](https://discourse.ladybug.tools/uploads/default/original/3X/9/e/9e4d893594eb913822617efa78d27b917760a03f.png)

Ideal Air System with NoEconomizer

 ![image](https://discourse.ladybug.tools/uploads/default/original/3X/e/0/e0163efccb6462286da8ef439667a5d0312e1400.png)