Zone Equipment Priority

I’m trying to a find a way to switch the order of the zone equipment with Ironbug. I’m modeling a system with a PTHP and a VAV diffuser in every zone. It defaults to the VAV for cooling first but I’d like the PTHP to be first. The ThermalZone params has a ZoneConditioningEquipmentListName which seems helpful, but there’s not much info. I tried a few different ideas without any luck. Any guidance would be appreciated, thanks!

image

Hi @avril14
You can right-click the thermal zone to uncheck the “Prioritize AirTerminal over ZoneEquipment”, this will put the PTHP before the air terminal:
image

1 Like