Honeybee_Energy_AFN_Natural Ventilation Load_ Output

@chris

Below are the list of outputs that I generally use to calculate the Load through ventilation, infiltration, exfiltration, mixing and others when I invoke AFN objects. Few of the HVAC based outputs give zero values when the zones are assigned with Natural ventilation.

I remember using volume flow rate output and heat transfer formula (Q=c×m×ΔT) in EP EMS to derive heat transfer into and from zone just from fenestrations.

HVAC,Average,AFN Zone Infiltration Sensible Heat Gain Rate [W]
HVAC,Average,AFN Zone Infiltration Sensible Heat Loss Rate [W]
HVAC,Average,AFN Zone Mixing Sensible Heat Gain Rate [W]
HVAC,Average,AFN Zone Mixing Sensible Heat Loss Rate [W]
HVAC,Average,AFN Zone Infiltration Latent Heat Gain Rate [W]
HVAC,Average,AFN Zone Infiltration Latent Heat Loss Rate [W]
HVAC,Average,AFN Zone Mixing Latent Heat Gain Rate [W]
HVAC,Average,AFN Zone Mixing Latent Heat Loss Rate [W]
HVAC,Average,AFN Zone Duct Leaked Air Sensible Heat Gain Rate [W]
HVAC,Average,AFN Zone Duct Leaked Air Sensible Heat Loss Rate [W]
HVAC,Average,AFN Zone Duct Leaked Air Latent Heat Gain Rate [W]
HVAC,Average,AFN Zone Duct Leaked Air Latent Heat Loss Rate [W]
HVAC,Average,AFN Zone Duct Conduction Gain Rate [W]
HVAC,Average,AFN Zone Duct Conduction Heat Loss Rate [W]
HVAC,Average,AFN Zone Duct Diffusion Latent Heat Gain Rate [W]
HVAC,Average,AFN Zone Duct Diffusion Latent Heat Loss Rate [W]
HVAC,Average,AFN Distribution Sensible Heat Gain Rate [W]
HVAC,Average,AFN Distribution Sensible Heat Loss Rate [W]
HVAC,Average,AFN Distribution Latent Heat Gain Rate [W]
HVAC,Average,AFN Distribution Latent Heat Loss Rate [W]
HVAC,Average,AFN Exfiltration Heat Transfer Rate [W]
HVAC,Average,AFN Zone Exfiltration Sensible Heat Transfer Rate [W]
HVAC,Average,AFN Zone Exfiltration Latent Heat Transfer Rate [W]
HVAC,Average,AFN Linkage Node 1 to Node 2 Mass Flow Rate [kg/s]
HVAC,Average,AFN Linkage Node 2 to Node 1 Mass Flow Rate [kg/s]
HVAC,Average,AFN Linkage Node 1 to Node 2 Volume Flow Rate [m3/s]
HVAC,Average,AFN Linkage Node 2 to Node 1 Volume Flow Rate [m3/s]

1 Like