Air flow volume output from HB Read results

@deepthi.ravi, @ElzineBraasch

You can usually find most outputs by searching the EP Input/Output reference, and using the HB components for searching and reading custom EP results. From the wind and stack
ventilation section, you can get the ventilation flow rate with the following output terms:

  • Zone Ventilation Current Density Volume Flow Rate
  • Zone Ventilation Standard Density Volume Flow Rate
  • Zone Ventilation Air Change Rate

You’ll want the “Current Density” flow rate, if you want the flow rate that’s effecting the zone heat balance, more detail on this here: