Hi!
An E+ question coming up, so maybe @chris you are the right person to address
I’m trying to limit the capacity of the DX single speed cooling coil and realize that there’s a discrepancy between the input “Rated Total Cooling Capacity” and the output “Cooling Coil Total Cooling Rate”.
Copied from the documentation on “Rated Total Cooling Capacity” as seen below, it’s stated that the capacity is based on fixed rated conditions:
" Field: Gross Rated Total Cooling Capacity
The total, full load gross cooling capacity (sensible plus latent) in watts of the DX coil unit at rated conditions (air entering the cooling coil at 26.7 °C drybulb/19.4 °C wetbulb, air entering the outdoor condenser coil at 35 °C drybulb/23.9 °C wetbulb, and a cooling coil air flow rate defined by field rated air flow rate below). […]."
Group Heating and Cooling Coils: Input Output Reference — EnergyPlus 8.7
Is there any way to make the “Cooling Coil Total Cooling Rate” output respect the coil capacity input given to the DX single speed cooling coil?