Glass material primary and secondary transmission
Is it possible to create a window build-up where I specify each glass layer’s inner/outer emissivity (longwave) and inner/outer absorptivity (shortwave), as well as solar transmission, in order to account for re-radiated absorbed solar energy? I want to account for the solar absorption in order to measure the surface temperature of my windows.
If this isn’t possible, can I create a complex fenestration system in e.g. LBNL WINDOW and import this as my window constructions?
Thanks!
Joe
@jroberts Hi! Here is some relevant information:
In EnergyPlus, the absorptivity of a window glazing layer is not directly input as a single parameter in the WindowMaterial:Glazing object. Instead, it is derived from the solar and visible transmittance/reflectance values that you specify.
Here’s how it works:
Relevant fields in WindowMaterial:Glazing
  • Optical Data Type (SpectralAverage, Spectral, SpectralAndAngle)
  • Solar Transmittance at Normal Incidence
  • Front Side Solar Reflectance at Normal Incidence
  • Back Side Solar Reflectance at Normal Incidence
  • (similar fields for visible and IR ranges)
Relationship:
For solar radiation, absorptance is computed as:
α=1−τ−ρ\alpha = 1 - \tau - \rhoα=1−τ−ρ
where:
  • τ\tauτ = Solar Transmittance (at normal incidence)
  • ρ\rhoρ = Solar Reflectance (front or back, depending on direction)
This is wavelength‑averaged if you use SpectralAverage, or calculated across wavelengths if you supply Spectral Data.
Example (SpectralAverage glazing):
idf
WindowMaterial:Glazing,
  Clear 3mm,              !- Name
  SpectralAverage,        !- Optical Data Type
  ,                       !- Window Glass Spectral Data Set Name
  0.837,                  !- Solar Transmittance at Normal Incidence
  0.075,                  !- Front Side Solar Reflectance at Normal Incidence
  0.075,                  !- Back Side Solar Reflectance at Normal Incidence
  0.898,                  !- Visible Transmittance at Normal Incidence
  0.081,                  !- Front Side Visible Reflectance at Normal Incidence
  0.081,                  !- Back Side Visible Reflectance at Normal Incidence
For this glass:
  • Front absorptance = 1−0.837−0.075=0.0881 - 0.837 - 0.075 = 0.0881−0.837−0.075=0.088
  • Back absorptance = 1−0.837−0.075=0.0881 - 0.837 - 0.075 = 0.0881−0.837−0.075=0.088
and Output Variables applicable:
Per-Surface Window Absorbed Solar Radiation
  • Surface Window Transmitted Solar Radiation Rate [W]
  • Surface Window Absorbed Solar Radiation Rate [W]
  • Surface Window Absorbed Solar Radiation Rate per Area [W/m2]
  • Surface Window Absorbed Shortwave Radiation Rate [W]
  • Surface Window Absorbed Shortwave Radiation Rate per Area [W/m2]
  • Surface Window Absorbed Beam Solar Radiation Rate [W]
  • Surface Window Absorbed Diffuse Solar Radiation Rate [W]
(these give total absorbed energy, split by beam/diffuse if desired)
Per-Layer (Glazing Layer) Absorptance
For multilayer glazing (e.g., double-pane, triple-pane), EnergyPlus can report absorbed solar by each layer:
  • Surface Window Absorbed Solar Radiation Rate Layer {i} [W]
  • Surface Window Absorbed Solar Radiation Rate Layer {i} per Area [W/m2]
where {i} = glazing layer index (1 = outside pane, 2 = inside pane, etc.)
Optical Properties / Absorptance Coefficients
If you want the actual absorptivity values, not just absorbed energy:
  • Surface Window Transmitted Solar Radiation Fraction
  • Surface Window Reflected Solar Radiation Fraction
  • Surface Window Absorbed Solar Radiation Fraction
These fractions are basically:
Example Output:Variable block
idf
Output:Variable,
  *,  !- Key Value (all surfaces)
  Surface Window Absorbed Solar Radiation Rate per Area,  !- Variable Name
  Hourly;  !- Reporting Frequency
Output:Variable,
  Surface Window Absorbed Solar Radiation Fraction,
  Hourly;
Output:Variable,
  Surface Window Absorbed Solar Radiation Rate Layer 1,
  Hourly;
Hopefully some of that is helpful!
Thanks Trevor,
That’s really helpful! It looks like in honeybee-energy glass construction the shortwave absorptivity is calculated like you say as \tau_sol - \rho_sol, whereas the longwave emissivity is input directly. I guess we don’t really care about the back solar reflectance.
  • shortwave transmittance _transmittance_
  • shortwave reflectance _reflectance_ (front only)
  • longwave transmittance _t_infrared_
  • longwave emissivity _emiss_front_
  • longwave emissivity _emiss_back_
Thanks for helping me get my head around this!