Honeybee / EnergyPlus sizing error: PsyPsatFnTemp temperature out of range
Hi everybody! My master thesis simulation is driving me insane…
AUT_NO_Amstetten.110180_TMYx.epw (1.5 MB)
debug.gh (56.0 KB)
SchoolModel - Pre retrofit - Natural ventilation.gh (214.5 KB)
rhino model Gofile - Cloud Storage Made Simple
whenever I run a simulation I get this warning:
Program Version,EnergyPlus, Version 2
5.1.0-1c11a3d85f, YMD=2026.03.23 13:50,
************* Beginning Zone Sizing Calculations
** Warning ** Temperature out of range [-100. to 200.] (PsyPsatFnTemp)
** ~~~ ** Routine=CalcPurchAirLoads, During Sizing, Environment=AMSTETTEN HEATING DESIGN DAY 99.6% CONDNS DB, at Simulation time=01/21 24:00 - 24:10
** ~~~ ** Input Temperature=-461.96
************* ===== Recurring Error Summary =====
************* ** Warning ** Temperature out of range [-100. to 200.] (PsyPsatFnTemp)
************* ** ~~~ ** This error occurred 1 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 1 times.
************* ** ~~~ ** Max=-461.964630 C Min=-461.964630
I tested both scenarios:
  • a predefined/base Honeybee program with working thermostat setpoints
  • a custom HB Setpoint object with simple constant heating/cooling setpoints
In both cases, as soon as the room is conditioned and has valid setpoints, the model enters sizing and the error appears:
During Sizing
What I found:
  • If the room is unconditioned, the error disappears.
  • If HVAC is assigned but there are no thermostat setpoints, Honeybee reports that the Ideal Loads Air System will not be translated.
  • If the room is conditioned and there is a valid setpoint path (either from a predefined program or from a custom setpoint object), the sizing error appears.
  • So the trigger seems to be the conditioned-zone sizing path with valid thermostat setpoints, not only a custom setpoint object.
  • The issue occurs during sizing, not during the normal run period.
Software:
  • Ladybug Tools version: 1.9.4
  • EnergyPlus version: 25.1.0
The debug script is an extremely reduced version where I tried to cut the script as much as possible to identify the culprit, but I am really lost.
Many thanks to whoever is going to give me some help!
Hi, Did you find a fix. I am not sure i am having a similar problem and everytime i run the simulation i get different result and not by small variations, huge variations.
I couldn’t find a fix but my values make sense and are repeatable after every simulation. I kept digging into the issue and since it’s just a warning that happrns during sizing and not affecting the simulation I am just ignoring it. I can safely say that specific error is not the cause of your results being unpredictable.