I am running a simple ideal air HVAC test to see if a given set of temperature and humidity setpoints can be achieved and visualizing the results in hourly plots. The simulation is for a museum so the setpoints need to be met at all times.

I am getting two distinct errors but nothing is flagging on the components.

  1. Unmet hrs are showing 0 even though the temperature plot shows temperatures outside the temperature setpoint range (and outside of 1.1 deg C tolerance). It also does this when i use the custom outputs of:

Zone Heating Setpoint Not Met Time
Zone Cooling Setpoint Not Met Time

Do unmet setpoints hrs only analyse occupied hrs?

Do unmet hrs analyse and report time periods when the HVAC system is off?

is there a way of reporting total hrs outside of a temperature and humidity range?

  1. Based on the temperature hourly plot, the ideal air system seems to be switching off during unoccupied times or times of low occupancy. Its my understanding that this should not be happening. (I have constant schedules for temperature and humidity) What could be the cause of this?

422 ironbug script.gh (735.2 KB)

Hi @chris, @mostapha, @AbrahamYezioro I wanted to bump this as i have run in to more issues with the hourly plot. This time i am showing temperature above a range as red, within the range as green and under the range as blue. This is what the hourly plot looks like. This being pulled straight from the EPW file.

image

However when i interrogate the data with a conditional statement like this which should correlate with the green in the hourlyplot you can see i am getting very different results.

The hourly plots a great graphical representation tool but i find i am not able to trust them anymore. Here is the gh file.

Hourly plot discrepency.gh (45.8 KB)

cheers, Nick

Not sure if this is what you are after:


If so, the statement you defined misspelled one of the β€œ<” characters.
Can it be?
-A.

You are absolutely right. My apologies! this was done late last night. Should have looked at it with fresh eyes this morning.

Did you see also the issues with the unmet hrs visualisations in my earlier post?

The default thermostats in Ladybug Tools are set to control air temperature (like most real-worlds thermostats). Not operative temperature, which includes the effects of all the surfaces in the room. So it’s very common to have the air setpoint met but the operative temperature is outside of those range because of sun falling on the surfaces, heat conducting out of poorly insulated glass, etc.

This is one of the many reasons why simply meeting the thermostat setpoint does not guarantee thermal comfort of the occupants.

2 Likes

Thanks for your clarification Chris!