Manage to test HVAC system 13 RadiantCeiling and DOAS with a single zone model. Always receive the error message as follows. Please help (note the script has been tested working for some template systems, such as sys02 PTHP, sys16 VRF+DOAS).

@MingboPeng please help. I am having same error even after adding component names.

Thanks @Aayushi @CheneyChen for reporting. I will check this issue in a few hours and keep you posted.

Hi @CheneyChen @Aayushi,

I am able to recreate this issue when I use a room that has no “INTERNAL SOURCE” construction applied correctly. So after you applied the construction for “INTERNAL SOURCE”, you have to use the new rooms for creating an HBModel.

You can also use this sample file that I have a room added to the system.
Note: document is set to Meter.
20230502_Room with Radiant Panel_MP.gh (77.7 KB)

Thank you for responding, @MingboPeng. I could use your script without any errors. But, I am facing the same error again when I try to specify the ‘Radiant Surface Type’ to be Floors instead of Ceilings. I tried making this change along with changing the Internal Source Component (exterior floor instead of exterior roof), and without changing Internal Source Component. In both trials, it shows the same previous error. Also, this building has only radiant Heating and no cooling system. I was planning to model this by changing the High Air Temperature to 100 or some very high number so that cooling never kick off in the simulation. I am not able to attach GH file or a screenshot as a new user on this platform. Can you please help to solve this? Thank you very much in advance!

Hi @Aayushi, I suspect that the construction wasn’t set correctly. I would suggest you visualize the constructions for each face so that you can see if everything is set correctly.

Hi @MingboPeng,

I am having a similar issue to the one posted here. I am trying to model a radiant floor for cooling only. However, I see no difference in the operative temperatures, which are selected as the temperature control type. Could you please point out what I am doing wrong?
Test room with Radiant Panel.gh (91.8 KB)

Thanks,
Julio

Hi @MingboPeng ,
Is there any way to simulate radiant cooling systems in Ironbug? like the one defined above. I have tried step by step all the options and nothing seems to work.

Thanks

Hi @Julioamodia89, in your gh file. I found two critical errors that prevents the radiant system working correctly.

The RadiantSurfaceType can only be ONE value: Ceilings, Floors, or CeilingsAndFloors, when you have ONE room.

You are using the same name for two constructions, which totally confused the model how it should be set up.


After I add a new name for interior floor, the simulation works correctly. I checked the ceiling’s interior surface temperature, the result makes sense to me.

Here is the same surface temperature without any system.

Here is the fixed file that I ran in case you want to have a test on your side.
Test room with Radiant Panel_MP.gh (132.8 KB)

Thank you @MingboPeng
That did the job!

Hi All - I ran into a similar issue and had a slightly different resolution. The Ironbug template for Sys13 includes internal source definitions for Interior Floor but does not include Ground Floor - I had to add this to get it to work (see screenshot below)