Modelling steel studs with batt insulation Honeybee

Hey everyone!

I’m trying to figure out the best way to model a steel stud wall with internal insulation in honeybee.

What’s the recommended approach for representing the steel studs and the insulation? Should I account for the thermal bridges explicitly, or is there a simplified method people usually use?

Hi @ajassoi , there are a couple options that you might decided to utilize, depending on the goal / use / phase of the model, and who you are preparing it for:

  1. Estimate: Steel-studs generally yield a 50%-60% reduction on the resistivity of the cavity insulation. So for example: if you are using mineral fiber with an approximate R-4/inch, just cut that in half and use that for your cavity layer.
  2. Use the calculation method from AISI S250-21 | North American Standard for Thermal Transmittance of Building Envelopes With Cold-Formed Steel Framing, 2021 Edition This can work pretty well to calculate an equivalent thermal conductivity for your stud layer - and allows you to factor in the effects of stud gauge, spacing, continuous exterior insulation, etc… If you would like to see an example, I implemented most of this calculation in a module which is part of the Honeybee-PH extension: honeybee_ph_utils/aisi_s250_21.py which you could probably re-purpose for your needs.
  3. Use the AHRAE HoF Ch-27 ‘Zone’ method to calculate the equivalent thermal conductivity of your stud-layer.
  4. Use the ASHRAE 90.1 Appendix A values from one of the tables. I usually use the Table A3.1-4 “Effective R-Values for Insulation/Framing Layers Added to Above-Grade Mass Walls and Below-Grade Walls” values, which isn’t quite right - but is pretty close and good enough for lots of scenarios.

Unless you are doing some sort of compliance model, or the effect of the studs is a core part what you are testing with your models - I’d say you can get plenty close by just applying a 50 or 60% derate factor though.

all the best of luck with it!
@edpmay

3 Likes

Hey @edpmay, thanks so much for your response!

Hi @ajassoi to add to @edpmay’s awesome info, there is a useful website with pre-thermal simulated constructions and thermal performance values:

best
-trevor