Hello everyone,
I’m a university architecture student working on a building energy simulation project using OpenStudio and EnergyPlus.
I’m experiencing an unusual result: the annual cooling load is approximately 19.6 times higher than the heating load, even though my building is located in Rochester, Minnesota (ASHRAE Climate Zone 6A, Cold-Humid).
I’m trying to determine whether this is caused by incorrect model settings or by the building’s internal heat gains and envelope characteristics.
1. Model information
-
Location: Rochester, Minnesota, USA (Climate Zone 6A)
-
Weather data: TMYx 2011–2025 EPW
-
Building type: Two-story educational and research facility
-
Total floor area: Approximately 4,508 m²
-
Window-to-wall ratio: 40%
-
Space Types: ASHRAE 90.1-2019 College (Classroom, Office, Laboratory, Corridor, Restroom, Stairs)
-
HVAC: Ideal Air Loads
-
Construction Sets: College-based construction sets
The intended thermostat schedule is:
-
Weekdays, 08:00–20:00: Heating 21°C / Cooling 24°C
-
Weekday nights: Heating 15°C / Cooling 27°C
-
Weekends: Heating 15°C / Cooling 28°C
I have not yet fully verified whether the actual thermostat schedules and HVAC settings are correctly applied to every thermal zone.
2. Simulation results
The OpenStudio Results report shows:
-
Annual cooling load: 294,572.54 kWh
-
Annual heating load: 15,051.15 kWh
-
Cooling-to-heating ratio: 19.57:1
Some unusual monthly results:
| Month | Average outdoor temperature | Cooling load | Heating load |
|---|---|---|---|
| January | -7.9°C | 13,609 kWh | 5,197 kWh |
| February | -8.8°C | 14,492 kWh | 4,255 kWh |
| July | 22.3°C | 22,950 kWh | 0 kWh |
| September | 17.2°C | 37,040 kWh | 0.61 kWh |
Cooling demand is higher than heating demand even during the coldest winter months. September also has a much higher cooling load than July.
3. What I have checked
In OpenStudio:
-
Design Specification Outdoor Air objects are assigned to all College Space Types.
-
For the Office Space Type, the outdoor airflow per person is approximately 0.00236 m³/s-person.
-
Space Infiltration Design Flow Rate fields are empty in both Space Types and individual Spaces.
-
Space Types and Thermal Zones appear to be assigned to the appropriate rooms.
-
I have not yet confirmed whether the outside boundary conditions, internal loads, and Ideal Air Loads outdoor-air settings are all correct.
I also tested the model using a much colder weather file (Verkhoyansk, Russia) as a diagnostic comparison. The heating load increased substantially, but cooling loads remained significant.
4. My questions
-
Is such a high cooling-to-heating load ratio plausible for an educational building in Climate Zone 6A?
-
Could missing infiltration objects cause the heating load to be severely underestimated?
-
Does the Ideal Air Loads system automatically account for the outdoor air specified in the Space Types, or are additional settings required?
-
Could incorrectly assigned outside boundary conditions (such as Adiabatic instead of Outdoors) explain this behavior?
-
Which EnergyPlus output variables or OpenStudio settings should I inspect first to identify the source of the excessive cooling load?
I would really appreciate any guidance on diagnosing this issue.
I can provide screenshots of the monthly load profiles and relevant OpenStudio settings, as well as the OSM model file if needed.
Thank you very much for your help!