Unexpected temperature flattening with AirBoundaries

I’m running into some unexpected behaviour when using AirBoundaries in Honeybee models.

When setting an Air Boundary, Honeybee automatically adds ZoneMixing objects between the connected zones, assuming an air speed of 0.1 m/s.

In my tests with two identical, unconditioned zones and no internal loads, I found that once the wall is set as an AirBoundary, the temperature profiles of the two rooms become somewhat flattened. If I manually remove the ZoneMixing object from the IDF, the temperature profiles start to make more sense, representing an average of the two zones’ conditions before they were connected, and the results also match those of a merged single-zone model. With zone mixing assigned, I would have expected just a faster averaging between the zones, not such a dampening of their peaks.



What seems like an incorrect balancing in the airflows when using ZoneMixing may actually be more of an EnergyPlus issue than a Honeybee one, that’s why I first posted about it here on Unmet Hours.
However, since AirBoundaries are commonly used in Honeybee, and since ZoneMixing is automatically assigned to them, I thought I’d ask here in case others have noticed similar results.

This also reminds me of another issue I looked into a while ago involving CO₂ dilution with ZoneMixing. There too, the exchanged air appeared to distort the mass balance showing strange results in terms of CO₂ concentration. That post is here.

Would love to hear your thoughts.

Hi @chris

I was hoping you could take a look at this since it feels like a pretty significant issue, as air boundaries are such a common object in Honeybee and they’re particularly important for some projects I’m working on.

Another user has already done some testing and reported it on the EnergyPlus GitHub (post), so your input there would probably carry a lot of weight too.

HI @MatteoMerli ,

Sorry for not seeing this when you first posted and for it taking so long for me to respond.

You sparked quite a good discussion on Unmethours and congratulations on reporting an issue that has resulted in an EnergyPlus GitHub issue. I am pasting it here for reference if others want to follow whether anything comes of it:

It would seem that this is a situation that can happen when you have AirBoundary adjacencies between two rooms where the surface area of the AirBoundary is particularly high in relation to the volume of the rooms (like your screenshot). This results in the room mixing over more air in a timestep than it actually has in its total volume.

I think we would all agree that E+ should at least be giving a severe warning in this case if not providing a better auto-correction for this effect. So I hope that E+ GitHub issue eventually gets a response.

Did you try the suggestion given at the bottom of the unmethours post of just increasing the timestep? You can use the _timestep_ input of the HB Simulation Parameters component to boost the timestep all of the way up to 60 and then see if you still notice the effect.

The other option for working around this is to change the air_mixing_per_area input on the AirBoundary Construction used by Honeybee. It’s not exposed on any component but you can see here in the Honeybee SDK that the AirBoundary Construction has a property for this, which you can change from the default value of 0.1 m3/s-m2. So you would just have to create that construction inside of a GHPython component and assign it to all of the faces in your Honeybee Model that have an air boundary.

I’m not quite at the point that I would change the air mixing of the default AirBoundary construction in Honeybee if only because these cases of very high AirBoundary-area-to-Zone-volume ratio tend to be rare in models of real buildings. So I wouldn’t want the real-world cases to suffer because some of the more abstract test cases we have come up with are inaccurate. Also, for those needing really accurate simulations, upping the timestep is always a good suggestion, which seems to eliminate this effect as far as we can tell. Let me know if you feel strongly otherwise, @MatteoMerli .

Hi @chris,

Thanks a lot for following up on this!

Yes, I have tested increasing the timestep to mitigate this damping effect and, depending on the model, it either makes it disappear or just reduces it, confirming that the issue is tied to how much air is exchanged within a timestep.

What helped me clarify things was identifying the relationship between the three involved variables: u = air speed across the AirBoundary (m/s), t = timesteps per hour, and V/A = ratio between the smaller zone’s volume and the AirBoundary surface area.

This is then used to compare the air volume exchanged during one timestep and the volume of the smaller zone. Therefore:

  • If > 1 → more than 100% of the zone air is exchanged within a single timestep → inaccurate results.
  • If < 1 → the exchanged volume is smaller than the zone’s volume → physically consistent results.

I plotted this air-mixing-flow/room-volume ratio for different V/A values and for each possible EP timestep t, using Honeybee’s default air mixing speed u = 0.1 m/s. This allows to see which combinations of V/A and timestep lead to physically consistent conditions. Note that if changing the air speed, the graph curves shift and the allowable V/A scales proportionally (half of the air speed → double the allowable V/A).

For example, from the graph, considering the default timestep of 6, all models with V/A ratio < 60 would give inaccurate results, and based on my experience they are not that uncommon. Many models I have seen have V/A ratios between 5 and 30 (whenever one of the room sides is set as an AirWall). In those cases, only timesteps > 15 would give accurate results (and for the lower ratios, even t = 60 would not be enough). These simplified and more abstract test cases were only meant to isolate issues I noticed in more complex models that I unfortunately couldn’t share in the forums.

Since I found this issue, I have tried avoiding AirBoundaries as much as possible. When I cannot avoid them, I use that equation to evaluate how much I need to increase the timestep and/or reduce the air speed (which may also be more realistic in some cases).

That said, this is currently limiting some of our studies (e.g., large atriums or big spaces that cannot be modelled as single zones), so it would be great to see it addressed by the EP developers, and in the meantime get a waning implemented to inform of this current limitation.

Thanks, @MatteoMerli .

In this case, why not use the workaround that I listed here?

You can make a custom GHPython component that takes the model you are about to simulate and replaces all of the air boundary constructions with ones that use no flow rate or a smaller flow rate.

Thanks @chris. Yes, that’s a valid workaround, but only up to a certain extent. For large spaces where one or more sides are modelled as AirBoundaries, the V/A ratio becomes small requiring either a very high timestep or a near-zero flow rate.

Also, increasing the timestep up to 60 in complex models significantly increases simulation time and for example limits studies that involve multiple iterations. It also limits the possibility of simulating forced air mixing between rooms at higher air speeds, that is what I was investigating before my CO2 post.

Just to clarify, I don’t think there is much that can be done on the HB side, except maybe making users aware of this limitation and inform about the tuning options. It seems to be a structural limitation in EP related to the stability of the air mass balance equation, which I consider quite serious, so I’ll follow up on GitHub!

Hi @MatteoMerli ,

I looked closer at your calculations of V/A and did some of my own. I see your point that it is relatively easy for people to create situations where, even at a the finest simulation timestep of 60, the default air mixing at a rate of 0.1 m/s across air boundaries creates cases where more air than the room volume is mixed for the timestep. This means that the default simulation timestep of 6 easily causes over 10 times the room air volume to be mixed.

So it’s not as rare of a problem as I initially thought. That is, at least while we use a default air mixing flow rate of 0.1 m/s in honeybee, which I still think is a pretty typical indoor air speed to for buildings heated/cooled by all-air HVAC systems.

Also, I didn’t mean for it to sound like there isn’t anything that can be done on the honeybee side. It’s for reasons like this that I left the ability to create custom AirBoundaryConstructions within the honeybee-energy SDK. But I can see that the number of people for which this unbalanced air mixing is an issue is greater than the number of people who know how to use the honeybee SDK to correct the issue.

So I added a new method here that automatically lowers the flow rates across the model’s air boundaries for each room where the total flow rate across the air boundaries in the timestep exceeds the room volume:

You can get core libraries with this method on your end if you run the LB Versioner now. After that, you can open up this sample .gh file that I put together, which calls the method and allows you to see the resulting flow rates as you change the timestep:


test_balance_air_flows.gh (49.5 KB)
Note that this sample .gh file only works well when the model is in meters.

@MatteoMerli ,
If you can test this sample file and component against your cases and confirm that it is giving you the expected results, I will change the methods used to translate Honeybee models to OpenStudio/EnergyPlus to always run this method to balance the air boundary air flows before it performs the translation to OSM/IDF. That should give you and me some temporary peace of mind until the issue is eventually addressed in EnergyPlus.

If I don’t get any other feedback on the Grasshopper file that I put together here, I am going to just change the default behavior of writing OSM/IDF to use this new balance_air_boundary_flows method in the translation process.

I’ll do this by the end of this week unless anyone posts feedback sooner than that.

Hi @chris,

This is a great addition!

I was only able to do a quick round of tests on some shoebox models with different volumes and air boundary areas. Your component is assigning flow rates in line with what I would expect, and the temperature flattening seen with the default air speed seems resolved.

I’ve attached the results for one case at different timesteps with and without the correction. The default setup shows clear flattening (especially at lower timesteps), while the corrected one gives stable results. That said, in this case, simply increasing the timestep already mitigates much of the dampening.

One point to consider is that while the correction works around the numerical issue, the reduced flow can no longer represent a fully mixed condition. Don’t know if it would be helpful to show the final air mixing values to users, maybe in the validate component or elsewhere.

Many thanks for implementing it and hopefully the whole air mixing behaviour will be eventually reviewed in EnergyPlus.

FYI, I have made the running of this balance_air_boundary_flows method a standard part of translation to OpenStudio/EnergyPlus:

So, if you run the LB Versioner, @MatteoMerli , you should find that you no longer get any “temperature flattening” from the use of air bounadries.

As for this:

I imagine that the main reason why someone would use air boundaries in their model is because they are trying to account for the fact that the air is NOT well mixed between two adjacent spaces and they want to understand the difference in temperature and/or loads that result from this.

If people want to model a set of rooms as well mixed, there are better ways to do this that don’t require you to use AirBoundaries:

  1. Model the whole set of rooms as a single room with one closed volume around everything.
  2. Use the HB Set Zone component to make all of the Honeybee Rooms a part of the same EnergyPlus Zone. Zones in EnergyPlus are always assumed to have a single well-mixed air temperature.