Hi IronBug folks, I think I’ve found an issue. I’m trying to set up a DOAS AirLoop using a UnitarySystem so I can have integrated geo source heat pump coils.
I’ve stumbled on a configuration thing - it seems in order to use SetPoint control type for a UnitarySystem (rather than set a control zone which doesn’t make sense for DOAS) you have to then also specify the fields related to No Load Supply Air Flow Rate. (I confimed this separately debugging with OpenStudio) However I am seeing errors trying to force these settings in IronBug
When I try to set the “method” for No Load Supply Air Flow rate I get error at Air Loop level:
When I instead try to Autosize the flow rate I get error at ObjParam level:
It only works when I hard set the flow rate to a number:
Also attached .gh and model input hbjson
MS_DD_02.hbjson (422.7 KB)
MS_hvac_01.gh (257.4 KB)
Thanks!