Hi, I am trying to model a lab building where I do not want the air to be re-circulated. In the HB default systems, there was an option of setting that to “False”. How can I do the same in the ironbug system??
Hi @ApoorvGoyal,
Yes, creating a 100% constant schedule for the Maximum Fraction of Outdoor Air Schedule Name will make this Outdoor Air Controller 100% outdoor air/ no recirculation.
Here is an example:
20201004_AllOutdoorAir.gh (11.3 KB)