I would like to schedule the heating and cooling on/off.
I have decided to use the VRF system type of HeatCool HVAC Templates in reference to this.
However, I cannot find any schedule settings for heating and cooling on/off.
In Figure 1, Idealair, heat_avail and cool_avail is present and can be set to turn on or off heating and cooling. Not in HeatCool HVAC(2).
The component in Figure 3 allows setting values, but is there a way to set on/off?
Hello!
the _type_limit_ input is what you are looking for I believe.
from the docstring also has some more information, I’ve attached below
_type_limit_: A text string from the identifier of the ScheduleTypeLimit to
            be looked up in the schedule type limit library. This can also be a
            custom ScheduleTypeLimit object from the "HB Type Limit" component.
            The input here will be used to validate schedule values against
            upper/lower limits and assign units to the schedule values. Default:
            "Fractional" for values that range continuously between 0 and 1.
            Choose from the following built-in options:
                * Fractional
                * On-Off
                * Temperature
                * Activity Level
                * Power
                * Humidity
                * Angle
                * Delta Temperature
                * Control Level
HB Apply Room Schedules will allow you to apply schedules for setpoints rather than single values
Hello!
Thanks for your reply.
I don’t know where to connect the schedules for that component.
setpoint_sch seems to only be able to set the temperature.
(1. Solution exception:Heating Setpoint schedule should be in Temperature units. Got a schedule of unit_type Dimensionless.)
Please tell me where to connect it.
OH this sounds like setpoint schedule must be a temperature, we may not be able to use on/off for the setpoint schedule. It looks like I was incorrect about this that is my mistake.
ok!
Any help would be much appreciated!
If anyone knows, please let me know.
Using Ironbug would give you a much finer level of detail and allow to specify equipment availability schedules which I think you might be after if I’m not mistaken. There is also a template for VRF+DOAS. a tutorial series on using ironbug can be found here
Hello!
I tried ironbug.(No detailed settings.)
However, the heating and cooling load is not calculated.
Ideally, I would like to set it to produce a value similar to the VRF of the HB.
Please let me know if you know where to correct this.
Hi!
Supplementary information,
I want to create a room air conditioner for home use.
However i can’t find the corresponding templates.
So I decided to use this as a reference to set up a VRF.
https://discourse.ladybug.tools/t/how-can-i-creat-a-split-system-air-conditioner-in-honeybee-ladybug-tools-1-4/18085)
If you know of a better way(HB and ironbug etc) than this, please let me know.
Maybe just setting your setpoint values unrealistically high or low, so they never turn on your HVAC system, could work? E.g. heating for -20°C and cooling for 99°C for those hours where you don’t need them:
setpt_setb_cheat.gh (8.8 KB)
I will try that method.
Thank you!