the _type_limit_ input is what you are looking for I believe.
from the docstring also has some more information, I’ve attached below
_type_limit_: A text string from the identifier of the ScheduleTypeLimit to
be looked up in the schedule type limit library. This can also be a
custom ScheduleTypeLimit object from the "HB Type Limit" component.
The input here will be used to validate schedule values against
upper/lower limits and assign units to the schedule values. Default:
"Fractional" for values that range continuously between 0 and 1.
Choose from the following built-in options:
* Fractional
* On-Off
* Temperature
* Activity Level
* Power
* Humidity
* Angle
* Delta Temperature
* Control Level
HB Apply Room Schedules will allow you to apply schedules for setpoints rather than single values
OH this sounds like setpoint schedule must be a temperature, we may not be able to use on/off for the setpoint schedule. It looks like I was incorrect about this that is my mistake.
Using Ironbug would give you a much finer level of detail and allow to specify equipment availability schedules which I think you might be after if I’m not mistaken. There is also a template for VRF+DOAS. a tutorial series on using ironbug can be found here
I tried ironbug.(No detailed settings.)
However, the heating and cooling load is not calculated.
Ideally, I would like to set it to produce a value similar to the VRF of the HB.
Please let me know if you know where to correct this.
The component in Figure 3 allows setting values, but is there a way to set on/off?
Maybe just setting your setpoint values unrealistically high or low, so they never turn on your HVAC system, could work? E.g. heating for -20°C and cooling for 99°C for those hours where you don’t need them: